sizing power factor

Status
Not open for further replies.

jaykool

Member
Location
NE
Is there an easy way to size KVAR cap banks for 480V, 3phase motors?

I have a 200HP motor with an associated 35KVAR cap bank, (2) 12.5KVAR and (1) 10KVAR. How can I verify if this is accurate...going for 95% power factor.

Assume no nameplate data on motor.
 

bob

Senior Member
Location
Alabama
Is there an easy way to size KVAR cap banks for 480V, 3phase motors?

I have a 200HP motor with an associated 35KVAR cap bank, (2) 12.5KVAR and (1) 10KVAR. How can I verify if this is accurate...going for 95% power factor. Assume no nameplate data on motor.

Usually the mfg will give you the proper size. Are you trying to correct the facilities power factor?
 

bob

Senior Member
Location
Alabama
Mivey
I've never tried this but you could measure the power factor of the motors and use that to correct the PF of the whole facility. That might prove to be very time consuming if the motors are loaded at different times.
 

jaykool

Member
Location
NE
This is an existing application, the caps are shot and we are replacing. We only have 12.5KVAR caps...therefore install 3 for a total of 37.5KVAR. I know this is not a "big" deal. Just wondering if there was a quick way to ballpark KVAR needed without looking up in tables.
 

dkarst

Senior Member
Location
Minnesota
There are certainly "easy" ways like a spreadsheet on this site... but as an earlier poster replied, for a machine this size you need some real data if there is no nameplate. Undercorrecting doesn't get the job done in terms of money saved if you are trying to reduce a low PF charges from POCO and overcorrecting can cause serious technical consequences and damage equipment.

I guess if you were in an emergency, if you made some reasonable assumptions like a motor FL efficiency of 95% (which I looked up for a new 4 pole 200HP motor, your's may be different depending on a number of factors) and a existing power factor of 0.87, then 35KVAR of caps corrects you back to 0.95 which is your goal.

I can't stress enough the need to
1. Get some real data on the situation instead of guessing or assuming
2. It takes maybe 3 minutes to draw a power triangle and perform the above calculation.... until you are adept at this, I would stay away from "easy" methods such as spreadsheets or tables
 

Besoeker

Senior Member
Location
UK
Just wondering if there was a quick way to ballpark KVAR needed without looking up in tables.
I don't think so.
As an example, on one of our current projects there are two 225kW (300 hp) motors driving pumps. We are building the starters for those motors.
The main contractor is supplying the motors and pumps. Some way into the project, the proposed motor was changed. The first had a power factor of 0.84. On the second (also 225kW), it was 0.76.
Our PFC capacitors went from 70kVAr to 120kVAr because of that change. So not really in the same ballpark.
 

Besoeker

Senior Member
Location
UK
I have a 200HP motor with an associated 35KVAR cap bank, (2) 12.5KVAR and (1) 10KVAR. How can I verify if this is accurate...going for 95% power factor.

Assume no nameplate data on motor.
One further thought on this.....
If there is no nameplate data, how can you be sure it is a 200 hp motor?
 

drbond24

Senior Member
Assume no nameplate data on motor.

I'm with Besoeker on his question; if there is no nameplate data how do you know it is 480 V, 3 phase, 200 hp?

Anyway, in order to figure what power factor you are correcting to, you must know what power factor you are starting at. If you don't have it on the nameplate you'll have to measure it. You could assume a starting power factor, but then this is just getting silly. Your answer wouldn't mean anything. We need to know where you are starting to tell you where you are going on this one.
 

jaykool

Member
Location
NE
My bad, there is nameplate data...but nothing referencing power factor.

I was looking at a capacitor selection table...how do you know what your "uncorrected power factor" is?
 

ohmhead

Senior Member
Location
ORLANDO FLA
My bad, there is nameplate data...but nothing referencing power factor.

I was looking at a capacitor selection table...how do you know what your "uncorrected power factor" is?

Well use your motor name plate E X I X 1.73/1000=KVA


Now measure your watts with wattmeter on that motor running this is your true power KW .

KW/KVA = power factor
 

glene77is

Senior Member
Location
Memphis, TN
This is an existing application, the caps are shot and we are replacing. We only have 12.5KVAR caps...therefore install 3 for a total of 37.5KVAR. I know this is not a "big" deal. Just wondering if there was a quick way to ballpark KVAR needed without looking up in tables.

Jay,
Are you saying that you plan to connect the 3 caps in series to obtain a 37.5KVAR rating?

That would make the effective Capacitance
to be 1/3 of what you think.
And that would be 1/3 of the required PF correction.

:)
 

Besoeker

Senior Member
Location
UK
Well use your motor name plate E X I X 1.73/1000=KVA


Now measure your watts with wattmeter on that motor running this is your true power KW .

KW/KVA = power factor
Given that you know from the nameplate that it's 200hp or 150kW output*, you don't need to measure the power. In any case, the motor might not be running at full rated power at the time of the measurements.

*plus about 5% for losses to get input power.
 

Besoeker

Senior Member
Location
UK
Jay,
Are you saying that you plan to connect the 3 caps in series to obtain a 37.5KVAR rating?
I would assume that each 12.5 kVAr unit is three-phase.
If they are, each unit is most likely three capacitors in a delta configuration.
Not easy to connect three such units in series.
 

ohmhead

Senior Member
Location
ORLANDO FLA
Given that you know from the nameplate that it's 200hp or 150kW output*, you don't need to measure the power. In any case, the motor might not be running at full rated power at the time of the measurements.

*plus about 5% for losses to get input power.

Well i agree he doesnt have to with no load on that motor it would be a inductance with little resistance but when a loaded it would give him a wattage to go by .

Increased current while fully loaded and running makes watts the old right triangle formula to get VARS needed .

If he had a wattmeter on that motor it would give him a way to check his power factor .

Let me understand this more what would you do in this case to test a motor for power factor correction .

Iam here to learn also dont take this the wrong way iam interested in this .

Iam just a electrician and may need help here also ?


Just wondering about how one knows about what losses are know inside that motor without it running ?
 
Last edited:

Besoeker

Senior Member
Location
UK
Well i agree he doesnt have to with no load on that motor it would be a inductance with little resistance but when a loaded it would give him a wattage to go by .

Increased current while fully loaded and running makes watts the old right triangle formula to get VARS needed .

If he had a wattmeter on that motor it would give him a way to check his power factor .

Let me understand this more what would you do in this case to test a motor for power factor correction .

Iam here to learn also dont take this the wrong way iam interested in this .

Iam just a electrician and may need help here also ?


Just wondering about how one knows about what losses are know inside that motor without it running ?
I'm not quite sure what you are asking so I'll do my best.
The nameplate data gives rated current and voltage. From that you can calculate input kVA.
The nameplate also gives rated output power.
Add 5% or thereabouts for losses abd you have input kW.
Input kW/input kVA gives you input pf.
 

ohmhead

Senior Member
Location
ORLANDO FLA
Well Besoeker i guess iam a old time electrician ii always thought load needed to be a factor with a motor .

I know amperage draw of a motor is not a good test for power factor.

I always thought you really needed to run at full load to check all losses ?

We would measure fully loaded motors and test & record A&B VOLTS B&C VOLTS C&A VOLTS and also IA IB IC given PF- A PF- B PF- C

We then add v1+v2+v3/3= volts

IA+IB+IC+/3= AMPS

PFA+PFB+PFC/3=PF Then use PF=EXIXPFX1.73/1000=KVA

Then used hp x746 kw

KW/KVA =PF by measuring i did not know you could do it any other way i know today they have test equipment to do all this but just wondering how to do it on paper with out a motor running is different ?

Iam interested in your thoughts i have read your posts and know you deal with drives and design work with motors so help me understand this better .

input /output ?
 
Last edited:

Besoeker

Senior Member
Location
UK
Well Besoeker i guess iam a old time electrician ii always thought load needed to be a factor with a motor .

I know amperage draw of a motor is not a good test for power factor.

I always thought you really needed to run at full load to check all losses ?
On most, or possibly all, of the larger motors I have dealt with (500kW/750hp up) there would be a works test at full load and performance noted. Among other things, that would give losses and power factor usually at 2/4, 3/4, and 4/4 of full load rating.
For smaller machines, there is usually published manufacturer's data if it is a standard machine. Some will have been given a full test but it would be uneconomic to do every single one.
We would measure fully loaded motors and test & record A&B VOLTS B&C VOLTS C&A VOLTS and also IA IB IC given PF- A PF- B PF- C

We then add v1+v2+v3/3= volts

IA+IB+IC+/3= AMPS

PFA+PFB+PFC/3=PF Then use PF=EXIXPFX1.73/1000=KVA
This gives you kVA which you could have determined directly from nameplate voltage and current.

Sqrt(3)*VL*IL/1000

Then there is the question of how you know the motor is fully loaded. It is quite difficult to measure output power after the motor is installed. Output is torque multiplied by rotational speed. You can fairly easily measure rotational speed to within about 1 rpm. Torque is a whole lot more difficult. So you'd probably take full load to be when the motor is drawing full load current - which you got from the nameplate. Along with nameplate voltage.
Then used hp x746 kw
Again, where did you get the hp rating?
I'm sure you see what I'm getting at.

Iam interested in your thoughts i have read your posts and know you deal with drives and design work with motors so help me understand this better.
I appreciate that, thank you.
But you make me more than I am.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
One of the problems with using anything off the nameplate is that it states the PF at full load. At lighter loads the PF drops, sometimes by a whole lot.

Its not impossible to have 80% of FLC at 20% of mechanical full load. You can imagine what the PF is in such a case.

Best bet is to size off the nameplate and hope for the best. Its a bit of a crap shoot, and to get the whole plant in line at 95% is going to probably require some automatic capacitor banks somewhere.
 