Is there an easy way to size KVAR cap banks for 480V, 3phase motors?
I have a 200HP motor with an associated 35KVAR cap bank, (2) 12.5KVAR and (1) 10KVAR. How can I verify if this is accurate...going for 95% power factor. Assume no nameplate data on motor.
Would be good but:Usually the mfg will give you the proper size. Are you trying to correct the facilities power factor?
Assume no nameplate data on motor.
I don't think so.Just wondering if there was a quick way to ballpark KVAR needed without looking up in tables.
One further thought on this.....I have a 200HP motor with an associated 35KVAR cap bank, (2) 12.5KVAR and (1) 10KVAR. How can I verify if this is accurate...going for 95% power factor.
Assume no nameplate data on motor.
Assume no nameplate data on motor.
My bad, there is nameplate data...but nothing referencing power factor.
I was looking at a capacitor selection table...how do you know what your "uncorrected power factor" is?
This is an existing application, the caps are shot and we are replacing. We only have 12.5KVAR caps...therefore install 3 for a total of 37.5KVAR. I know this is not a "big" deal. Just wondering if there was a quick way to ballpark KVAR needed without looking up in tables.
Given that you know from the nameplate that it's 200hp or 150kW output*, you don't need to measure the power. In any case, the motor might not be running at full rated power at the time of the measurements.Well use your motor name plate E X I X 1.73/1000=KVA
Now measure your watts with wattmeter on that motor running this is your true power KW .
KW/KVA = power factor
I would assume that each 12.5 kVAr unit is three-phase.Jay,
Are you saying that you plan to connect the 3 caps in series to obtain a 37.5KVAR rating?
Given that you know from the nameplate that it's 200hp or 150kW output*, you don't need to measure the power. In any case, the motor might not be running at full rated power at the time of the measurements.
*plus about 5% for losses to get input power.
I'm not quite sure what you are asking so I'll do my best.Well i agree he doesnt have to with no load on that motor it would be a inductance with little resistance but when a loaded it would give him a wattage to go by .
Increased current while fully loaded and running makes watts the old right triangle formula to get VARS needed .
If he had a wattmeter on that motor it would give him a way to check his power factor .
Let me understand this more what would you do in this case to test a motor for power factor correction .
Iam here to learn also dont take this the wrong way iam interested in this .
Iam just a electrician and may need help here also ?
Just wondering about how one knows about what losses are know inside that motor without it running ?
On most, or possibly all, of the larger motors I have dealt with (500kW/750hp up) there would be a works test at full load and performance noted. Among other things, that would give losses and power factor usually at 2/4, 3/4, and 4/4 of full load rating.Well Besoeker i guess iam a old time electrician ii always thought load needed to be a factor with a motor .
I know amperage draw of a motor is not a good test for power factor.
I always thought you really needed to run at full load to check all losses ?
This gives you kVA which you could have determined directly from nameplate voltage and current.We would measure fully loaded motors and test & record A&B VOLTS B&C VOLTS C&A VOLTS and also IA IB IC given PF- A PF- B PF- C
We then add v1+v2+v3/3= volts
IA+IB+IC+/3= AMPS
PFA+PFB+PFC/3=PF Then use PF=EXIXPFX1.73/1000=KVA
Again, where did you get the hp rating?Then used hp x746 kw
I appreciate that, thank you.Iam interested in your thoughts i have read your posts and know you deal with drives and design work with motors so help me understand this better.