I am going to be pulling seven 12 gauge THHN wires (six current carrying and a ground) and am trying to figure out what size schedule 80 conduit would be required.  It looks like I am ok using 3/4 pvc to do this. I come up with the wires having a size of .0931 in sq and the 3/4 conduit having a total fill of .164 in sq.  Am I ok to do this or do I have to adjust for heat?
It's going to be a 240 volt wall heater circuit, and 120 volt bath receptacle circuit, a 120 volt sump pump circuit and a 120 volt lighting circuit. The bath and sump pump circuit will share a neutral.
Thanks for any advice.
	
		
			
		
		
	
				