They may be feeders, they may be secondary conductors but they are still taps.
The reason this becomes important is when someone wants to tap these taps.
I think there is a common misconception that the code says you "cannot tap a tap." It doesn't say that anywhere.
What it does say is that conductors supplied under the provisions of 240.21(A) through (H) shall not supply any other conductor except through an OCPD. This includes not only taps and transformer secondary conductors, but also conductors from generator terminals and battery conductors.