The pictures of lugs that your posting would never be installed on 100, 150, or 200 amp breakers. And if installed in a main lug only panel, they still are both lug and termination. The lug is the termination.iwire said:dnem said:I wasn't talking about changing the lugs. The lab temp rating is based on the weakest link in the panel, which usually is the lug. But if you change the lug you just end up with a panel with no UL listing.
No not necessarily.
I can change lugs on many panel boards, a common reason to change lugs is from single barrel lugs to stacker lugs.
Like these
![]()
dnem said:What if the lug wasn't the only reason that the panel had the lower temp rating ? Replacing the lug only leaves a question mark.
Exactly what Jim was pointing out, installing higher temp rated lugs will not raise the temp rating of the equipment.
dnem said:Since the lug is part of the breaker, you can't change the lugs on the breaker, you can only replace the breaker.
You don't do much commercial work do you?
Yes you can change the lugs on the breaker.
The reason this has to be done sometimes is to get the right lugs for the conductors being used.
Say I have a 400 amp breaker, it may have arrived with lugs rated for one 600 Kcmil each. However I might chose to run three sets of 1/0 copper. To do that I have to get lugs to accept that combination.
dnem said:The breaker temp rating of the breaker applies to the whole breaker including the lugs.
It may or may not.
dnem said:There is no separation between the breaker and the lugs on the breaker.
Often there is a separation there is a breaker with a rating and a lug or terminal with a rating.
Keep in mind that a breaker may be used without lugs at all, it may be bolted right to bus bars at one or both ends.
You're getting confused because you're not reading the whole post and then concluding that I "don't do much commercial work".
I actually don't do Commercial work any more, I'm too busy inspecting it.
I'm not concerned with large gear on this thread. Go back to the beginning and read what's been posted. You'll see what this thread is about. Have you seen a 100 amp breaker with removable lugs ? Your pictures belong on another thread. You're not replying to the subject of the thread.
I have yet to see prints for large gear that doesn't include wire size specs. I'm talking about 100, 150, or 200 amp small Commercial jobs that are just panel changes or possibly panel and minimal other work. These small jobs are where newer contractors get "their teeth cut".
If I would rather discuss this subject in a public forum rather than one on one with a contractor after giving them a red tag, then that's what I'll do.
Please read everything before you post on a thread.
David