We have two large storm water pumps; one pump is fairly new, the other is probably >50 years old with no nameplate. The pump & motor specs are as follows:
Pump #1
Size: 18" x 10', 8,200 gpm
Motor: 40 HP, 3 Ph, 230 V, 100 A, 1.15 SF, 117 SFA, 84.3 PF, Code F
Pump #2 (best estimates)
Size: 16" x 8.5', ~5,000 gpm (est)
Motor: 30 HP (est), 3 Ph, 230 V, 60 A
Both motors are powered through soft-starters which ramp up the starting current.
These pumps keep our commercial property from flooding. One time, we experienced a blackout and had to scramble to rent a transportable 70kW generator to power the pumps during a heavy storm. After that, a decision was made to install a diesel-powered standby generator.
Our general manager had some early discussions with a used generator broker. Based on their communications, he had thought that a 40kW generator would meet our needs. At the time, I ran some locked-rotor current calculations on our pumps (562 LRA & 421 LRA) and advised that the 40kW generator he wanted to purchase was undersized based on the generator's spec of being able to "start a 20HP, 3-Ph, Code G electric motor" (316 LRA).
Some time later, a local contractor was purchasing two 60kW generators and we were given the opportunity to add a third 60kW unit onto that purchase at a discounted price. We purchased that generator (ratings & specifications attached as PDF files).
After installing the generator, we discovered that it would not start our 40HP pump #1. In fact, it sounds like it's straining somewhat when starting our ~30HP pump #2. We contacted the generator distributor thinking there's something wrong with the generator, but they simply stated that their 60kW generator was too small to start a 40HP motor.
I then contacted two major brand-name generator manufacturers to see what generator they'd recommend for starting our pump #1. Both companies ran calculations using the motor nameplate data and other info; one company recommended a 60kW generator, the other recommended 50kW generator.
I have since spoken to a gentleman at a generator service & testing company. He stated that the power rating of a generator is not enough to determine it's suitability to a load. For example, he told me that the power of the diesel engine driving the alternator can influence whether or not it can handle a large step-load. That makes sense. But how could a 50kW rated standby generator outperform our 60kW rated standby generator? And why does it seem that our 60kW generator is straining to even start our 30HP pump?
At this point, we're trying to determine if the generator we purchased is defective or simply incorrectly-sized for our application.
Pump #1
Size: 18" x 10', 8,200 gpm
Motor: 40 HP, 3 Ph, 230 V, 100 A, 1.15 SF, 117 SFA, 84.3 PF, Code F
Pump #2 (best estimates)
Size: 16" x 8.5', ~5,000 gpm (est)
Motor: 30 HP (est), 3 Ph, 230 V, 60 A
Both motors are powered through soft-starters which ramp up the starting current.
These pumps keep our commercial property from flooding. One time, we experienced a blackout and had to scramble to rent a transportable 70kW generator to power the pumps during a heavy storm. After that, a decision was made to install a diesel-powered standby generator.
Our general manager had some early discussions with a used generator broker. Based on their communications, he had thought that a 40kW generator would meet our needs. At the time, I ran some locked-rotor current calculations on our pumps (562 LRA & 421 LRA) and advised that the 40kW generator he wanted to purchase was undersized based on the generator's spec of being able to "start a 20HP, 3-Ph, Code G electric motor" (316 LRA).
Some time later, a local contractor was purchasing two 60kW generators and we were given the opportunity to add a third 60kW unit onto that purchase at a discounted price. We purchased that generator (ratings & specifications attached as PDF files).
After installing the generator, we discovered that it would not start our 40HP pump #1. In fact, it sounds like it's straining somewhat when starting our ~30HP pump #2. We contacted the generator distributor thinking there's something wrong with the generator, but they simply stated that their 60kW generator was too small to start a 40HP motor.
I then contacted two major brand-name generator manufacturers to see what generator they'd recommend for starting our pump #1. Both companies ran calculations using the motor nameplate data and other info; one company recommended a 60kW generator, the other recommended 50kW generator.
I have since spoken to a gentleman at a generator service & testing company. He stated that the power rating of a generator is not enough to determine it's suitability to a load. For example, he told me that the power of the diesel engine driving the alternator can influence whether or not it can handle a large step-load. That makes sense. But how could a 50kW rated standby generator outperform our 60kW rated standby generator? And why does it seem that our 60kW generator is straining to even start our 30HP pump?
At this point, we're trying to determine if the generator we purchased is defective or simply incorrectly-sized for our application.