Sizing system bonding jumper

Status
Not open for further replies.
You are being obtuse.

I am. :)

I was just trying to defend Infinity a little seeing as how if "cross sectional area" isn't mentioned along with simply multiplying width times height, then that suggestion isn't it either. :)

A door may be 3 feet wide and 84 inches high, but, that doesn't tell me how thick it is.

No offense.

I'm sure they'll get the jumper all worked out.

JAP>
 
Semantics. Each of you is picturing the bus in a different orientation.

Cross-section area is a product of the two smaller dimensions.

When discussing a conductor's size, we aren't talking about its length.
 
But as you wrote previously, T250.102 tells him how to figure the size and your suggestion isn't it. As I stated, bus width times bus height gives the area, then chapter nine tables to find a conductor/s that have the equivalent area. Conductor size is based on the size of the conductors, not the amperage of the overcurrent protection.
This is for a temporary fix so my method is fine but for arguments sake once I have the cross sectional area of the bus where in the NEC will I find the ampacity of that bus?
 
Semantics. Each of you is picturing the bus in a different orientation.

Cross-section area is a product of the two smaller dimensions.

When discussing a conductor's size, we aren't talking about its length.

That's the whole point Larry.
The cross-sectional area must be mentioned somehow.

You can't simply say multiply the width times the height.

JAP>
 