You are being obtuse.And if I'm looking at the face of it, width x height is not going to tell me how thick it is.
JAP>
You are being obtuse.And if I'm looking at the face of it, width x height is not going to tell me how thick it is.
JAP>
You are being obtuse.
This is for a temporary fix so my method is fine but for arguments sake once I have the cross sectional area of the bus where in the NEC will I find the ampacity of that bus?But as you wrote previously, T250.102 tells him how to figure the size and your suggestion isn't it. As I stated, bus width times bus height gives the area, then chapter nine tables to find a conductor/s that have the equivalent area. Conductor size is based on the size of the conductors, not the amperage of the overcurrent protection.
Semantics. Each of you is picturing the bus in a different orientation.
Cross-section area is a product of the two smaller dimensions.
When discussing a conductor's size, we aren't talking about its length.