A alsw Member Aug 26, 2007 #1 112.5 KVA 480 DELTA to 208WYE XO TO BUILDING STEEL .WHAT SIZE CONDUCTOR. 75KVA 480 DELTA to 480 WYE XO to BUILDING STEEL.NEEDS WHAT SIZE CONDUCTOR.
112.5 KVA 480 DELTA to 208WYE XO TO BUILDING STEEL .WHAT SIZE CONDUCTOR. 75KVA 480 DELTA to 480 WYE XO to BUILDING STEEL.NEEDS WHAT SIZE CONDUCTOR.
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 26, 2007 #2 See 250.30(A)(3) and please turn off your Caps lock, it's considered yelling. Roger
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 26, 2007 #3 You need to provide us with the size of the secondary conductors to answer the question.
A alsw Member Aug 27, 2007 #4 112.5 KVA has 3/0 AWG Paralleled secondary conductors. 75KVA has 4/0 AWG secondary conductors
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 27, 2007 #5 Assuming that your secondaries have copper conductors: #3/0=167,800 circular mils 167,800(2)=335,600 circular mils (335.6 kcmil) Table 250.66 Over 3/0 through 350 kcmil= #2 copper Both transformers would require a #2 copper GEC.
Assuming that your secondaries have copper conductors: #3/0=167,800 circular mils 167,800(2)=335,600 circular mils (335.6 kcmil) Table 250.66 Over 3/0 through 350 kcmil= #2 copper Both transformers would require a #2 copper GEC.