I started a new job last week and found out that one of the previous electricians and the HVAC mechanic ordered VFD?s for some older pump motors for the boilers. They (HVAC mechanics) are having problems with the pipes shaking at startup and they also want to control the amount of flow. I believe the VFD?s were sized according to their horsepower. I?ve never sized VFD?s before and I?m concerned that these VFD?s will fail if installed.
These motors are 25 years old, and here is the information of the name plate:
Volts 230/460 (we are running at 460)
Amps 74/37 (the motors are currently drawing between 41-43 amps, but the HVAC said this is because they have a valve controlling flow. If he opens the valve, the amps will go back to 37)
HP 30
3-phase 60 hz
1. First will the VFD?s enable the motors to start slowly and rev up? If it?s possible, will the motors burn out quickly?
2. Can the motors be run below 50 hz? If not, I believe it will severely limit the amount we are able to control flow. Am I correct?
3. Does the VFD take the place of the starter? Is any additional overload protection required?
4. Is the sizing of the VFD?s and the control wiring usually sent to engineer, or does the electrician and HVAC mechanic usually size it?
Thanks in advance,
Frank
These motors are 25 years old, and here is the information of the name plate:
Volts 230/460 (we are running at 460)
Amps 74/37 (the motors are currently drawing between 41-43 amps, but the HVAC said this is because they have a valve controlling flow. If he opens the valve, the amps will go back to 37)
HP 30
3-phase 60 hz
1. First will the VFD?s enable the motors to start slowly and rev up? If it?s possible, will the motors burn out quickly?
2. Can the motors be run below 50 hz? If not, I believe it will severely limit the amount we are able to control flow. Am I correct?
3. Does the VFD take the place of the starter? Is any additional overload protection required?
4. Is the sizing of the VFD?s and the control wiring usually sent to engineer, or does the electrician and HVAC mechanic usually size it?
Thanks in advance,