I was always under the impression that both are sized per the nameplate specs. If I have a name plate that reads:
"Maximum overcurrent protective device - 25A"
"Minimum circuit ampacity - 18.1A"
That lets me put a 25A breaker in and I can run #12cu to the unit.
I'm struggling to decode the code article that allows that to be done. (referencing 2023 code)
I see 440.22(c)
"...........the protective device rating shall not exceed the manufacturers values marked on the equipment"
But for conductor size all I see is 440.32
"Branch circuit conductors supplying a single motor-compressor shall have an ampacity not less than the greater of the following:
-125% of the motor-compressor rated-load current
-125% of the branch-circuit selection current
So can they be sized separately from the OCDP and off the MCA or do the conductors need to be sized at 125% of the RLA?