Sizing wire and OCPD for HVAC/mini split systems

440.6(A)Exc 1 may be what yall’are looking for as far as MCA. And I agree, if nameplate states only max fuse size, that is what you are limited to by it’s listing and labeling.
 
Part V is for feeder short circuit/ground fault protection. I guess it depends on whether the question is about selecting conductor size or selecting overcurrent device? Without carefully reading through I can't recall but what little quick review I did I think I was assuming we were selecting the overcurrent device? A little of each going on throughout the thread.
No, we were selecting conductor size in the OP
 
From a recent thread:

 