For this sort of thing you REALLY HAVE TO do some soul searching and figure out what you ACTUAL load will be. ITs very unlikely to be more than half of what your load calc is. You will be throwing tens of thousands of someone's dollars down the toilet if you overestimate actual current draw. Assuming about 75 KVA which is 208 amps at 208 three phase is probably a decent start just for discussion purposes. at 480V, that is 90 amps, and I am showing 2 sets of 350 AL to be adequate. 350 URD quad is $5.95/foot from nassau national cable's website, and it will of course be cheaper than that with a quote and/or shopping around. So lets just say $5.50/ foot/ run so $11 per foot total. That is actually about the cost of 3 runs of 15KV #2 1/3 CN MV cable which i imagine is what you would use for a 15 KV run. Another option to MAYBE look at is using AL 2KV RHHW (PV wire) which is a very competitively priced cable. You would need about a single run of #4/phase. You would need to have 2000V transformers built but you could get a quote from say hammond ermco, or olsun. But likely it looks like just running the 480 is the way to go.