Sjo cord in pvc

Merry Christmas

JJWalecka

Senior Member
Location
New England
Have an injector pump with four float switches and two motors sjo. The plan that was discussed was a hole in the 3.5 foot cover...with Bell end down from LB..up the wall with PVC to injector pump controller.

Is it legal to run the sjo cord up the 2" pipe? Should I remove the sho cord sheath as it enters the 2" bell end?

Appreciate your insight
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Have an injector pump with four float switches and two motors sjo. The plan that was discussed was a hole in the 3.5 foot cover...with Bell end down from LB..up the wall with PVC to injector pump controller.

Is it legal to run the sjo cord up the 2" pipe? Should I remove the sho cord sheath as it enters the 2" bell end?

Appreciate your insight
These motors are less than 300V?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It’s a sleeve, not a conduit. If the pump comes with the cord, it’s meant to be used that way.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
As I've read on here before if the code doesn't say you can't then you can.
 