Re: sjow cord

Look at the two articles below. If it is for a permanent installation: No


400.7 Uses Permitted .
(A) Uses. Flexible cords and cables shall be used only for the following:
(1) Pendants
(2) Wiring of luminaires (fixtures)
(3) Connection of portable lamps, portable and mobile signs, or appliances
(4) Elevator cables
(5) Wiring of cranes and hoists
(6) Connection of utilization equipment to facilitate frequent interchange
(7) Prevention of the transmission of noise or vibration
(8) Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection
(9) Data processing cables as permitted by 645.5
(10) Connection of moving parts
(11) Temporary wiring as permitted in 527.4(B) and 527.4(C)
400.8 Uses Not Permitted .
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1) As a substitute for the fixed wiring of a structure (2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception: Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.8.
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted in this Code
 