Doesn't mean you couldn't run two feeders in a common raceway and use only one common neutral from what I can see. All conductors have to be in the same racway - this will result in needing to derate for number of current carrying conductors in the raceway and possible need to increase conductor sizes.
There is no requirement for a neutral with an feeder. Consider two feeders: 3-wire 480V delta and 208Y/120V.
Derating required: If might not effect wire size: 6 THHN #8 .8?55 = 44 next larger OCPD 50A