Hello all,

In SKM the arc flash calculations lists the switchboard as equipment type - Panel. I am trying to understand even though the equipment is called switchboard the software treat's them as panelboards ? I know it is the UL and ANSI standard which decides the type since it is bus gap dependent and it can be changed manually. But I am trying to understand why they called switchboard but treated as panelboard.
 
Hello all,

In SKM the arc flash calculations lists the switchboard as equipment type - Panel. I am trying to understand even though the equipment is called switchboard the software treat's them as panelboards ? I know it is the UL and ANSI standard which decides the type since it is bus gap dependent and it can be changed manually. But I am trying to understand why they called switchboard but treated as panelboard.

It likely has to do with the construction of the branch/feeder protective device connections. Most switchboard manufacturers simply mount standard panelboard interiors into very large steel enclosures.
 
Hello all,

In SKM the arc flash calculations lists the switchboard as equipment type - Panel. I am trying to understand even though the equipment is called switchboard the software treat's them as panelboards ? I know it is the UL and ANSI standard which decides the type since it is bus gap dependent and it can be changed manually. But I am trying to understand why they called switchboard but treated as panelboard.

I think SKM automatically selects "Panel" with a 25 mm arc gap for any low voltage systems, and "Switchboard" with a 104 mm gap for any high voltage systems. I don't they you can edit these (at least not on my version of SKM, which is an older version.)
 