Thermostat controlled water heater tanks also cycle on & off, yet are considered a continuous load. Same with 220.82(C)(6) HVAC loads.I wouldn’t consider a kiln a continuous load. The heating element is either cycled or otherwise limited to control the ramp up time.
220.14(A) may consider it nameplate, until the listed instructions, however poorly written, recommend 30A breaker or wire. NEC 110.3(B) requires the 30A circuit, regardless of continuous load, voltage drop, or other speculation.