Kent Andersom

New member
Is GFCI protection required for 120 volt refridgerators and freezers in commercial kitchens or is a single device permitted. I cannot find the code reference
 
Is GFCI protection required for 120 volt refridgerators and freezers in commercial kitchens or is a single device permitted. I cannot find the code reference


Welcome to the forum.

All GFI commercial kitchen requirements are in 210.8(B).




Edit to add: Missed those apple fritters again!
 
Kent,

As others have pointed out…

All 125-volt, single phase, 15- and 20-ampere receptacles installed in non-dwelling kitchens shall have ground-fault circuit-interrupter protection for personnel (08 NEC).

A definition for kitchen can be found in Article 100

Non-dwelling kitchens are governed under Section 210.8(B)(2). There are no exceptions to 210.8(B)(2). [...and the lack of language for this section leaves no wiggle room...]

As I understand this:

This means that:
Regardless of the receptacle’s accessibility, intended use, or application; the requirements of Section 210.8(B)(2) would apply to ALL said receptacles installed in a non-dwelling kitchen …


I hope this is helpful...


mweaver
 
Last edited:
Another angle is to use the customers existing security system and monitoring service if they have one.

You can get temperature monitoring devices that with proper panel programing send a silent message to the central station.

I have been working on a lot of security systems lately and many have temp alarms in sprinkler rooms to help prevent freeze ups.
 
What's a freeze up?

LOL, I guess that would be foreign to a guy from Florida.:smile:

Many times the fire pump / sprinkler room is only heated by a single heater, if that fails during the winter the room could drop below freezing and the water in the sprinkler pipes could freeze solid at first just blocking the flow but soon enough splitting the pipes open.
 
LOL, I guess that would be foreign to a guy from Florida.:smile:

Many times the fire pump / sprinkler room is only heated by a single heater, if that fails during the winter the room could drop below freezing and the water in the sprinkler pipes could freeze solid at first just blocking the flow but soon enough splitting the pipes open.

Gosh i sure miss the NORTH LOL. They have problems we never even think about.
 