Slash rated breaker

Status
Not open for further replies.

Lucas Organ

Member
Location
NL CANADA
Occupation
Industrial Electrician
Guys I have a slash rated breaker 60/75 degrees. Which degree column would I use out of table 2 CEC to size my wire?

Thanks looking forward to all the input
 
I’m probably sticking my nose where it doesn’t belong ( I don’t use CEC) but probably also depends on type of cable you are using, if it is a cable you are using, and also the equipment the conductors are terminating and what degree it’s rated for.
 
Guys I have a slash rated breaker 60/75 degrees. Which degree column would I use out of table 2 CEC to size my wire?

Thanks looking forward to all the input
Like I told you in the other thread, there is nothing in the CEC on this. Here is the bulletin from Ontario that allows us to use the higher rating.