mpd said:SE cable, aboveground use ONLY
And away we go.....
Actually it is not for direct burial.
See these are both opinions, one just as valid as the other.
mpd said:SE cable, aboveground use ONLY
mpd said:check the UL white book, SE cable is listed for aboveground use only
mpd said:iwire
i couldn't resist
check the UL white book, SE cable is listed for aboveground use only
mpd said:the problem with SER underground is the bare aluminum ground
mpd said:peter
do you think aboveground and underground are one in the same?
mpd said:iwire
I think the last debate on this dennis talked to a rep from southwire who told him the cable is not designed for underground
mpd said:but UF wire is permitted to be installed as NM, SE cable is not permitted to be installed underground
lordofpi said:I don't think the SE-underground debate can really be settled on this forum,
iwire said:Oh, as long as someone talked to salesman all my doubts are put aside. :grin:
I bet that same rep would say SER is not designed for installation in a raceway at all.....even though it is allowed.
Dennis Alwon said:Okay-- attack...
j_erickson said:But the 2008 NEC clears it up nicely: Uses not permitted: 338.12 A(2) "Underground with or without a raceway".