A anbm Senior Member Location TX Occupation Designer Sep 29, 2011 #1 Is there a minimum spacing requirement between two electrical sleeves and between sleeve and wall? Will 1 inch be enough? Thx
Is there a minimum spacing requirement between two electrical sleeves and between sleeve and wall? Will 1 inch be enough? Thx
A anbm Senior Member Location TX Occupation Designer Sep 29, 2011 #2 Can we group (3) 1" conduits into (1) 4" or 5" sleeve?
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Sep 29, 2011 #3 I'm assuming fire walls here, is there a penetration detail on the plans? If not you would need to check your state bldg codes which are most likely IBC chapter 7 driven.
I'm assuming fire walls here, is there a penetration detail on the plans? If not you would need to check your state bldg codes which are most likely IBC chapter 7 driven.
A anbm Senior Member Location TX Occupation Designer Sep 29, 2011 #4 conduits go through slab - 3rd floor
iMuse97 Senior Member Location Chicagoland Sep 29, 2011 #5 anbm said: Can we group (3) 1" conduits into (1) 4" or 5" sleeve? Click to expand... Sure thing.