N NorthwestPV Member Location Oregon, US Oct 29, 2015 #1 We need to install sleeves through a firewall for data and communications. Is there a distance that the sleeve must extend past the wall on each side?
We need to install sleeves through a firewall for data and communications. Is there a distance that the sleeve must extend past the wall on each side?
J JFletcher Senior Member Location Williamsburg, VA Oct 29, 2015 #2 Dont think so. STI and other companies make sleeve kits, and they only extend a few inches at most from either side. Here's a pic of an install I did years ago: https://www.flickr.com/photos/32712057@N06/3391627552/in/dateposted-public/ iirc, some firestops arent rated for cable bundles, so make sure you use the right stuff. I believe the cable in the pic has Hilti FS-1 in it.
Dont think so. STI and other companies make sleeve kits, and they only extend a few inches at most from either side. Here's a pic of an install I did years ago: https://www.flickr.com/photos/32712057@N06/3391627552/in/dateposted-public/ iirc, some firestops arent rated for cable bundles, so make sure you use the right stuff. I believe the cable in the pic has Hilti FS-1 in it.