Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
Hello,

I have to run 6-3 romex in a basement. I'd like to sleeve 6' of the 6-3 romex in conduit. What size EMT should I use and how do you determine this?

Thank you
 
I agree with Larry's response. If you were using the EMT as a raceway you would take the width of the NM cable, find the corresponding single conductor size, and then fill the EMT to no more than 53%.
 
If you were using the EMT as a raceway you would take the width of the NM cable, find the corresponding single conductor size, and then fill the EMT to no more than 53%.
Per Note 7 to Chapter 9 Table 1, for a single cable you can go up to 53%/0.8 = 66%.

Cheers, Wayne
 
If you use EMT or other metallic raceway, That section of raceway would need to be connected to an EGC per Art. 334.15 (C) Other than that, I agree with Larry also.
 
I think that you want to read that again. :)
Good point, the allowance in the second sentence is only for a single conductor, not for a single cable.

Is there any basis in physics for distinguishing--one conductor in a conduit can be up 66% of the area, but one cable can only be up to 53% of the area? Nothing comes to mind initially.

Cheers, Wayne
 
If you use EMT or other metallic raceway, That section of raceway would need to be connected to an EGC per Art. 334.15 (C)
If one end terminates in an outlet box, that will be taken care of.

(Does that only apply to EMT on walls, or in ceilings, too?)

If it's not terminated, another option is to use PVC instead of EMT.
 
If one end terminates in an outlet box, that will be taken care of.

(Does that only apply to EMT on walls, or in ceilings, too?)

If it's not terminated, another option is to use PVC instead of EMT.
I can see where you could interpret "walls only" as it mentions it in the section. But if you read the last sentence, it says, "Metal conduit, tubing, and metal outlet boxes shall be connected an EGC complying with the provisions of 250.86 250.148." It doesn't say whether these conduits are on the wall or the ceiling.
 
Around here, we don't even sleeve #6 nm drops because nobody sees that as subject to physical damage.

I'm curious also, why 6/3 to HVAC equipment?
It needs a neutral and ground?
I was wondering the same thing, 6-3 is what the engineer specified. I saw the equipment last night, and there is no neutral
 
Check 250.86 closely. Metallic conduit sleeves are not required to be connected to an EGC.
Nice catch Gus. Thinking along the lines of best practices vs. NEC (minimum standards), Is there a chance that the metal sleeve could become energized by a nicked conductor? I think I would connect the sleeve to an EGC because I would rather have that breaker trip rather than have the sleeve become energized.
 