So here it is Sunday, and I am working on some antique hot chassis radios. Dig out a transformer marked ans an isolation transformer for safety reasons.
For some reason I decided to make sure it was as marked. I found the following: 1) no continuity between the windings ( a good start). 2) When plugged in I went and checked from the load side to ground, her is where I am now lost...... One side of load receptacle was about 65 V to ground and the other about 16.
I am confused ...... What gives, I was expecting nothing to ground fro either leg.
Any ideas? ( no i didnt get out the megger to test the insulation, just a fluke 83 for continuity)
howard
For some reason I decided to make sure it was as marked. I found the following: 1) no continuity between the windings ( a good start). 2) When plugged in I went and checked from the load side to ground, her is where I am now lost...... One side of load receptacle was about 65 V to ground and the other about 16.
I am confused ...... What gives, I was expecting nothing to ground fro either leg.
Any ideas? ( no i didnt get out the megger to test the insulation, just a fluke 83 for continuity)