SMALL (150VA or less) isolation transformer

g-and-h_electric

Senior Member
Location
northern illinois
Occupation
supervising electrician
So here it is Sunday, and I am working on some antique hot chassis radios. Dig out a transformer marked ans an isolation transformer for safety reasons.

For some reason I decided to make sure it was as marked. I found the following: 1) no continuity between the windings ( a good start). 2) When plugged in I went and checked from the load side to ground, her is where I am now lost...... One side of load receptacle was about 65 V to ground and the other about 16.

I am confused ...... What gives, I was expecting nothing to ground fro either leg.

Any ideas? ( no i didnt get out the megger to test the insulation, just a fluke 83 for continuity)


howard
 
You're reading "phantom" voltages because your meter has a high input impedance.

Parallel a small 120v incandescent bulb with the meter and you'll read 0v to ground.
 
Coupling capacitance exists on all ungrounded systems. You should not expect valid voltages if you do not have a valid reference point.
 
You're reading "phantom" voltages because your meter has a high input impedance.

Parallel a small 120v incandescent bulb with the meter and you'll read 0v to ground.
To add, I use a solenoid tester (Knopp K60) for 99% of troubleshooting.
 