Small appliance ckts...05 code....

Status
Not open for further replies.

chevyx92

Senior Member
Location
VA BCH, VA
210.52(B)(1).......In the kitchen, pantry, breakfast room, dining room or similar area of a dwelling unit, the 2 or more 20 ampere small appliance branch circuits required by 210.11(C)(1) SHALL serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C) and receptacle outlets for refrigeration equipment.


Question is......If all you run is the 2 required small appliance ckts, then by the article above you can a put a receptacle in for a microwave, disposal and dishwasher on the small apliance ckts? It says shall serve all wall and floor outlets. I never do this but after reading that article, I want to know technically can you do it??? I think I am over looking something.
 
Bea, someone could comply with 210.23 and install a range hood on the SABC. 210.52(B)(2) is the key to this question, because it is the section that forbids receptacles not serving wall/counter/fridge receptacles from being included on the SABC circuit. :)
 