chevyx92
Senior Member
- Location
- VA BCH, VA
210.52(B)(1).......In the kitchen, pantry, breakfast room, dining room or similar area of a dwelling unit, the 2 or more 20 ampere small appliance branch circuits required by 210.11(C)(1) SHALL serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C) and receptacle outlets for refrigeration equipment.
Question is......If all you run is the 2 required small appliance ckts, then by the article above you can a put a receptacle in for a microwave, disposal and dishwasher on the small apliance ckts? It says shall serve all wall and floor outlets. I never do this but after reading that article, I want to know technically can you do it??? I think I am over looking something.
Question is......If all you run is the 2 required small appliance ckts, then by the article above you can a put a receptacle in for a microwave, disposal and dishwasher on the small apliance ckts? It says shall serve all wall and floor outlets. I never do this but after reading that article, I want to know technically can you do it??? I think I am over looking something.