Re: Small applience circuits and desk extensions of counter
I would be careful, Scott, you are asking for another 300 reply thread with statements like that.
First, if you read 210.52, it gives specifics for General Provisions, Small Appliances, Countertops, Bathrooms, ....
It does not define what a countertop is, yet it tells us what to do when encountering a countertop
in kitchens and dining rooms. So is a 'desk' a countertop when in a kitchen? If it is built in, and most likely made of the same material as the other countertops, then it is hard to say that it is NOT a countertop. Especially the ones that have a smaller base cabinet below on one or either side of the chair location. (I know some would disagree)
jwelectric has posted a link on a discussion about SA circuits in regards to this desk.
Your question is more specifically about GFI protection.
210.8(A)(6) kitchens - where the receptacles are installed to serve the countertop surfaces.
If you install an outlet for that surface, it should be GFI protected because it serves a countertop.
Now Scott, back to your point. If you install an outlet below and drill a hole through, is that outlet not serving the countertop? and what about your minimum spacing requirements for countertops?