Re: Small applience circuits and desk extensions of counter
Originally posted by aelectricalman:
Q: Can the plug be apart of the SA Circuit, yet be exempt from GFCI protection like that of a refridgerator on a SA circuit? IE, Line side it on the GFCI.
See, that's the problem desks give us. 210.52(B)&(C) are very specific (yet vague). Everything specified shall be on an SA circuit, and nothing else.
So if a desk is not counterspace, it's forbidden to install outlets powered by the SA circuit there. If a desk
is counterspace, it's required. When a condition is either forbidden or required, and it's unclear what to do, we've got a problem.
Reason being, the homebuilder doesnt want the GFCI to be inside of the doors of the desk cabinet. He wants it to be easily seen if there is a trip. This comes on the behalf of poor planning on his part, to add cabinets after the fact.
GFCI's are a protective device, not a customer convenience device.
Analogy: Safety glasses look dumb, and I'd like to protect my eyes without looking dumb. If I have to wear glasses by law, then my problem with looking dumb or finding the safety devices inconvenient plays second fiddle to the rule, IMO.
If the breaker on his surge protector trips, it'll probably be in a place where he'll have to get on his knees to reset it. Somehow I imagine he will pull through this hardship and be the stronger for it.