weressl said:...and I stand by there with you.
...It seems to me that the prevelant argument is that the NEC does not allow reduction of EGC. It seems that Okonite and all the other cable manufacturers are marketing cables that do not meet that requirement as they start reducing the EGC sizes at larger sizes.
Any comments?
I don't understand.
Table 250.122 allows considerably smaller EGC than circuit conductors.:-?