mshields
- Boston, MA
Involved in the design of a small, 5000 square foot apt building. Emergency lighting has been to this point, via battery packs.
Recently, while under construction, they come to realization that they're going to need a generator to back up a sump pump. And since they're going to have to put one in, they'd like to do the emergency lighting via the generator as well.
To my knowledge, if we put the emergency lighting on the generator, we'll need two ATS's and because we're in Massachusetts, MI cable for the "Emergency" function.
My question is this; we do a lot of hospitals. In 517, if you have a demand load of 150kW or less, you can go with one less ATS. I don't believe there is any such provision in Article 700. But I wanted to double check. It seems absurd to have two ATS's on what will be perhaps a 20kW unit.
Thanks,
Mike
Thanks,