When using a 20 amp circuit breaker to protect the installation of multiple receptacles and light fixture for a 120v service, can a 12 gauge branch be used and then tie in 14 gauge taps?
Then that makes the answer YES you can but you must protect it at 15 amps.No, for what you have described you must protect the circuit for the #14 AWG conductor at 15 amps.
Chris
Then that makes the answer YES you can but you must protect it at 15 amps.![]()