I need a K-6010 for a 200 amp CH
Mike, IYO, when must the calculation take place?
Roger
In 702 it tells us that the load is to be calculated
In 702 it tells us that the load is to be calculated so I would think that it would be required to be done before the inspection.
No Mike it does not say a calculation must be made, a calculation is one way. Again, a calculation or other approved methods, the other approved methods do not have to include any calculations.
Well Bob I bet with a little thought you can see the difference between a tripped circuit and a power failure.And how is that different from that same person plugging in their life safety equipment and say a space heater on the same branch circuit?
I don?t see anything that says anything different do you?
Well Bob I bet with a little thought you can see the difference between a tripped circuit and a power failure.
I would also wager that if you were the one on that oxygen concentrator that you would be saying something about wanting to know in your heart that the generator didn?t fail.
It is real easy for us to say that a 13kw generator will carry 54 amps and know what will and will not work but then again we aren?t the ones flopping around like a fish out of water when there is no power.
We need an english major. I think that the way the sentence is structured, that both the phrase "in accordance with Article 220" and the phrase "by another approved method" apply to the word "calculations". I have to agree with Mike that the rule requires calculations.
I still do not see it that way, there is an "OR" in there that surly means something. :smile:
And taken with the CMPs statement the intent is clear.
Common iwire. The sentence clearly says calculation have to be done by option one OR option 2. However I agree with Roger. When it comes to manual transfer the other approved means may have to be trial and error.
I still do not see it that way, there is an "OR" in there that surly means something.
And taken with the CMPs statement the intent is clear.
Then pray tell us just what it is if it is not coming up with a load? Both give us the same results and is an approved method that is found in Article 220.The CMP states that one of the approved methods may be a load reading, that is not a calculation.
In addition text has been added to indicate how the load is to
be calculated.
For instance if you are including the branch circuits in a home
that supply part of the general lighting load, how do you do that calculation.
The most logical approach is to use Article 220 and the new language makes
that clear.
However, it is recognized that a number of jurisdictions are allow
recorded load measurements and similar information to be used to provide the
capacity.
Then pray tell us just what it is if it is not coming up with a load? Both give us the same results and is an approved method that is found in Article 220.
The load can be determined by crystal ball or any other method that is acceptable to the AHJ.
Here is an installation I did last May under the 2008 NEC it left me, the customer and the inspector all with a warm fuzzy feeling. :smile:
![]()
I can not remember the KW of the genset but it certainly could not run everything in this large home, this main panel powers at least two sub panels, a steam generator, a pool central AC etc.
The owner is fully aware that he has to be selective when running the generator.
IMO I have not violated any NEC Article nor have I short changed this customer.
Are you disagreeing with me or agreeing with me? :-?
I feel Roger and I are pretty close to the same view.
The CMP states that one of the approved methods may be a load reading, that is not a calculation.
You tell me what calculation you envision that does not include Article 220?
This is a nonsense thread. You cannot control what the homeowner is going to do after you leave, fixed loads are almost NON-existent in residential, Doing ANY type of calculation is completely useless.