An air conditioning contractor was using a vacuum pump and received a shock when he touched the hose connection port of the pump. The motor for this pump was European Style (220 Volt to Neutral) and the power source was US style (120 volt to Neutral, 240 volt between phases). After investigating this incident, I found that the vacuum pump was connected to a 220 volt source using a 2 pin adapter, thus eliminating the grounding conductor, this being the primary cause of the incident. Upon further investigation the following items were noticed concerning this motor:
- Motor "On/Off" Switch was a single pole type
- Motor windings were megged and checked out good
- Windings resistance was very good
- A voltage of 110 Volts was measured between the case and ground without grounding conductor.
- Injured person was sweating profusely when the incident occurred
- Vacuum Pump had rubber posts underneath to absorb vibration
My question is not what caused this incident, but how we would rate the possible severity and what could be the possible cause of this high of a voltage occurring on this motor case, even in the "off" position with seemingly good winding insulation? What type of strength could this "Field" have concerning the severity?
:-?