This is somewhat out of normal type of work so I thought I'd ask to make sure I'm not over complicated it. I've got little, standalone dryer unit with a MOCP of 8.6A. Does this mean I have to put an 8A fuse or circuit breaker instead of a normal cable plugged into a wall outlet? It just seems odd to me that it'd be designed in such a way that the latter is not allowed. Full electrical specs below:
Electrical Data
Standard Power Supply 115/1/60 V/Ph/Hz
Nominal Electric Consumption 0.31 (3.1) kW (A)
Total Input Current 4.2A
Minimum Circuit Ampacity (MCA) 5.1A
Maximum Rating of Overcurrent Protective Device 8.6A
Fuse Max. 8.0A
Electrical Data
Standard Power Supply 115/1/60 V/Ph/Hz
Nominal Electric Consumption 0.31 (3.1) kW (A)
Total Input Current 4.2A
Minimum Circuit Ampacity (MCA) 5.1A
Maximum Rating of Overcurrent Protective Device 8.6A
Fuse Max. 8.0A