Hey all.
I work for the local utility. I have a customer who installed a pool and pool house with a spa and a gazebo (in addition to his unoccupied, almost finished 7000 sq. ft house). The electrician installed a 400A main breaker for the pool and pool house, however it's 500' ft away from the 25 kVA pole-bolted XFRM! His load doesn't look bad(2 1.5 hp pumps, some lighting for the gazebo and the small pool room/guest house). Normally, we as the utility won't allow a customer to go more than 250' from the point of connection. I was doing some VD calcs and came out to about 7% w/ a 500' run of 4/0 al. We are not supposed to allow more than 5% VD thru the secondary and service. That was NOT knowing what the NEMA code letter was on the 2 motors.
My question is, should he up the wire to 350mcm? Usually we won't go that big, but I'm thinking the electrician is going to have to run that anyways, short of moving his meter panel 250' closer.
I'm not an electrician, just a designer, but it seems to me it might be cheaper for the electrician to just move the panel.
Sorry for the long post.
I work for the local utility. I have a customer who installed a pool and pool house with a spa and a gazebo (in addition to his unoccupied, almost finished 7000 sq. ft house). The electrician installed a 400A main breaker for the pool and pool house, however it's 500' ft away from the 25 kVA pole-bolted XFRM! His load doesn't look bad(2 1.5 hp pumps, some lighting for the gazebo and the small pool room/guest house). Normally, we as the utility won't allow a customer to go more than 250' from the point of connection. I was doing some VD calcs and came out to about 7% w/ a 500' run of 4/0 al. We are not supposed to allow more than 5% VD thru the secondary and service. That was NOT knowing what the NEMA code letter was on the 2 motors.
My question is, should he up the wire to 350mcm? Usually we won't go that big, but I'm thinking the electrician is going to have to run that anyways, short of moving his meter panel 250' closer.
I'm not an electrician, just a designer, but it seems to me it might be cheaper for the electrician to just move the panel.
Sorry for the long post.