Small Shed Electrical Design
EBSoares
McKinney, TX
Electrical Engineer
Hi, all.
One of our high school projects has a small shed near the main building (separate building). The shed will have a motorized rollup overhead door (208V, 3ph), a couple of light fixtures (277V, but could be 120V if needed), and receptacles (120V) - for a total of 3 circuits. All the voltages required are available in the main building.
I was hoping someone might be able to help me with the following questions:
  1. Does the shed need its own separate grounding system (with a ground rod, ground bar, and all that) as per 250.32(A), or does the exception there apply, if we simply provide the three circuits from a panel at the main building?
  2. Does the shed need its own panel as well? It feels like overkill to provide a panel for just a shed.
  3. If a panel is not required and we can simply provide 3 individual circuits, does 225.31 apply, requiring that each each circuit have its own disconnect?
  4. Do you have any important tips for the electrical design of sheds?
Thanks in advance.
Edgar
Based on the loads, I think you need a feeder and a panel in the building and that will trigger a requirement for a grounding electrode system.
The only way around this would be to use a single 208Y/120 volt circuit to feed all of the loads. That would mean there are no separate overcurrent protective devices for the various circuits in the shed.
Not sure that is possible without knowing the actual loads.
The use of 277 for the lighting would complicate the installation a lot.
Yeah, I'm not seeing the use of two unrelated voltages, now you have two feeders or a transformer in the shed
If the roll up door was 480V, you could run a 480v and 208/120 branch circuit to the building. The only time you can have multiple branch circuits to a building is when they have different characteristics, such as differing voltages.
Running a feeder instead of a branch circuit pushes you to a ground electrode system.
Thank you, everyone - these are all very helpful and it's great you offered all these different ways at looking at the scenario.
If all we needed were lighting and receptacles, I could try a MWBC, but with the rollup overhead door I'm going to need another circuit... Looks like I'll need a panel and grounding system in there after all.
Cheers!
Edgar
I would suggest first doing a load calculation for all of the loads expected in the shed. Is this going to be a place were there will be extensive tool use, or a place for storage? How much power will the receptacles need to supply? Do you expect future loads (charging of equipment, etc.)?
Does the roll up door _require_ it's own 3 phase circuit? Or could it share the circuit with other loads or operate on single phase 120V?
If the total demand load is less than 7 KVA, then I'd try really hard to fit everything on to a single 20A 208/120V MWBC. This eliminates the need for a panel and GES.
Note that there is still a requirement to have a _disconnect_ in the detached structure the kills all power. If you run a 3 phase MWBC this could be as simple as a 3 pole toggle switch.
Thanks, @winnie, makes sense to review the total load to see if a simple MWBC would get the job done. We don't yet have the final load on that rollup door, so we are assuming worst-case scenario. But will check all my options, as we will be circuiting soon, so we will have all the loads.
Cheers,
I'd put a small panel in the shed.
It makes for a much cleaner install.
You'll never regret it.
Jap>