You shouldn't put a feoresonnant CVT like a Sola ahead of a VFD unless it is over sized by at least 200%. Ferroresonnant transformers will flat-top the sine wave as you approach full rated current, which results in low DC bus voltage when it passes through the rectifier and extreme heat in the CVT.The motor FLA 17.2 /sqrt 3 = 10 A ??? ( from his choke sizing post )
the drive is only rated for 6.7 output on 1 ph input?
the max S for the drive at 230/3 is sqrt 3 x 230 x 6.7 ~ 2.7 kva
converted to 208/1 is 13 A drive input
call it 15 assuming the pump is fully loaded and some drive loss
if really power quality perhaps a cvt like a sola
will maintain V, isolate THD both ways, reduce line noise, etc
i don't think it is power related, magnitude or quality