curt swartz
- San Jose, CA
- Electrical Contractor
I wanted to get some input from the members here that have experience in wiring small residential wells. Most of the projects I work on are served by municipal water systems but occasionally I work on jobs in the hills that require wells. On these projects we usually run a feeder to a small panel near the well and the well/pump contractor takes it from there.
I?m working on a project now that is totally off the grid (no electric, gas, phone or water services). We pulled a feed and installed a panel next to the well along with 3 GFCI protected receptacles for the UV filters. The plumbing contractor has a pump person on staff who is supposed to complete the rest of the wiring. One of the regular plumbers visited the job site a couple of weeks ago and installed the UV filters in the 3 storage tanks but didn?t install the float switches or do any of the wiring for the well pump. The Forman for the GC called the plumbing contractor and was told that his pump guy is very busy so just have the electrician finish the wiring.
I talked to the owner of the plumbing contractor and told him I at least want them to install the floats. I also asked if they were going to supply any type of pump controller or contactor. He said that no additional equipment was required since the contactor was part of the small pump control box that was already connected directly to the cable coming from the pump.
From what I have seen this box is usually just a capacitor for the pump. I went up the hill and took a look and sure enough the box is just a small relay and capacitor. It has 4 terminals that connect directly to the well pump cable and 2 terminals (L1 & L2) for the supply. The relay is just used to control the capacitor.
According to the label placed on the ?capacitor box? the FLA of the well pump is 7.8 amps @ 240 volts. I have no idea what the switch rating is of typical floats but is it normal to just have them switch the well pump motor load off directly without any type of contactor? Also do small well pumps typically require any type of external overload protection? I?m thinking even if the floats can handle the 8 amp motor load it would be better to have them control a contactor that controls the pump. If the pump requires external overload protection I would need to use a magnetic starter instead of a simple contactor. How do you guys normally deal with this type of installation?