jbolen

Senior Member
Is there an article in the NEC that states that smoke dictators have to be connected to each other.
 
There are 3 references likely in force by your local AHJ:

1. The building code (R313 of the IRC)

2. The NFPA 72 (Fire Alarm Code)

3. The manufacturer's installation instructions (NEC 110.3(B).)
 
Is there an article in the NEC that states that smoke dictators have to be connected to each other.

No, but I think you would be hard pressed to find a code that allows them NOT to be interconnected. Interconnection has been around for quite some time now...the only place I ever see a stand alone hard wired smoke detector is in apartments.
 