I will be wiring a duxple house soon and my question is do I have to interconnect the smokes in both units together? I have never wired a duplex so I have no clue
mdshunk said:(3) On each level of the dwelling unit, including basements
Exception: In existing one- and two-family dwelling units, approved
smoke alarms powered by batteries shall be permitted.
Yeah, NFPA goes into that more in the apartment building section. Seems like we usually end up using a regular cheap FA panel for the common areas in apartment buildings to handle the pull stations and so fourth.celtic said:Note that if there is "common area" (basements, stairwells, hallways) these smokes gt connected to themselves - NOT the units smokes - to the "house" panel.
mdshunk said:The section I quoted would apply more to townhouse units (or the OP's duplex example), where a basement and attic area would be only for each unit, and not a common area.
That's the way I read NFPA72, yes.celtic said:What IF .....
It is just a simple duplex/triplex?
No pullstations....no FACP...etc?
"Standard" 110v w/battery back up units?
Sounds like you've got it straight. For completeness sake, here's the section that prohibits cross-notification between units when the building is 3 or more dwelling units:dSilanskas said::smile: Its just a duplex house and the basement is split into two areas so I will connect each area basement with the smokes of that unit Thank you guys for your help
dSilanskas said::smile: Its just a duplex house and the basement is split into two areas so I will connect each area basement with the smokes of that unit Thank you guys for your help
celtic said:What IF .....
It is just a simple duplex/triplex?
No pullstations....no FACP...etc?
"Standard" 110v w/battery back up units?
mdshunk said:That's the way I read NFPA72, yes.
No common areas means no "building" FA system. Just regular hardwired interconnected smokes. Seems like you could have a 100 unit building, and if it had no common areas, there'd be no FACP. This isn't really an area I know much about, but I can read pretty well. :smile: I hope somebody will correct me if I have it wrong.
That doesn't seem to be the case, the way I read it, but I'm still trying to get my head around it. Matter of fact, it says that remote annunciation of the individual dwelling unit's "systems" is optional. I also don't see a horn/strobe requirement in each dwelling unit from the common area FACP. In fact, Annex A of NFPA72 suggests that the horn in the hallway is often sufficient notification from the building FA system. Any fire alarm guys here?celtic said:IF the property has "common areas" a FACP would be required...along with horn/strobes in the individual units tied into the FACP (common area devices) to notify the individual units...as well as an interconnect between the individual units back to the FACP for central station monitoring?
mdshunk said:Note that the notification requirement is for each dwelling unit (singular), and not all dwelling units. The notification requirement for apartment buildings (3 or more units) has more stricter language that prohibits cross-notification between dwelling units. For one and two family, it's not really prohibited, per se, but just not required.
True, that's a pretty fundamental code section that hadn't really crossed my mind for this sort of thing.wbalsam1 said:210.25 prohibits branch circuits from dwelling A from supplying devices, etc., in dwelling B. This includes all circuits...even smoke detectors. What a tenant does to his/her circuits cannot affect another tenant's circuits. :smile:
Is this basicly CO detection on the lowest sleeping level? Can it be complied with by substituting a combo smoke/CO detector for a regular detector location?Pierre C Belarge said:Lets not forget about CO Detectors. Starting January 1, 2008 there are new requirements in NYS regarding CO Detectors. The reference is Section 611 p. 43 of the Fire Code of NYS - 2007. This section has been completely revised and the changes are significant. (if not complied with, probably very costly as well)
mdshunk said:Is this basicly CO detection on the lowest sleeping level? Can it be complied with by substituting a combo smoke/CO detector for a regular detector location?[/quote]
No, the requirements in NYS have been completely revised - they used to take one paragraph, now the requirements are almost a full page. They are referenced at: Residential Code NYS and the Fuel Code of NYS.
Combination type detectors are permitted. Some locations may be different than for smokes. It is best to read the actual documentationfor location details.
wbalsam1 said:In NY State, CO detectors in new construction are required to be on a lighting circuit. This is no longer a requirement for the single and multiple station smoke detectors since they are required to have a battery backup. (It was a requirement under our old Title 9 code). So when contractors are putting their combination CO/SD in the hallway adjacent to sleeping rooms on the lowest level (that has sleeping) they must have the whole SD/CO circuit on a lighting circuit. If they opt to have strictly a CO detector on a circuit without the SD's, it must be on a lighting circuit. :smile:
And of course our "new" RCNYS (based on the 2002 NEC) will require AFCI protection of the "Entire" circuit for all 120 volt 15 & 20 amp outlets within the bedrooms. The exceptions noted at 2005 NEC 210.12 will not be allowed to be substituted in 1 & 2 family dwellings, but will be permitted in multiple dwelling buildings. :smile: