This isn't really a NEC question, but I'm betting a lot of you are familiar with fire alarm codes.
Is a smoke detector required in a elevator pit or at the top of the hoistway? There are no sprinklers in the elevator hoistway or anywhere around this elevator.
From NFPA 72, 3-9.3.4:
Steve
Is a smoke detector required in a elevator pit or at the top of the hoistway? There are no sprinklers in the elevator hoistway or anywhere around this elevator.
From NFPA 72, 3-9.3.4:
That seems to say they are not only not required, but prohibited (unless there is a sprinkler or smoke relief). But I don't understand why they would be prohibited in the hoistway.Smoke detectors shall not be installed in elevator hoistways.
Exception: Where the top of the elevator hoistway is protected by automatic sprinklers.
Exception: Where a smoke detector is installed to activate the elevator hoistway smoke relief equipment.
Steve