A zero amperage circuit mounted on the ceiling away from everything is in jeopardy of what??????? What are you protecting this from??? Exactly???????
Is that kind of a redundant statement, seeing how the only technology that is available is an AFCI circuit breaker?
And your point is.......??
YES THERE are a lot of beds and furniture pushed up against the smoke detectors this makes perfect sence in an asylum.
A zero amperage circuit mounted on the ceiling away from everything is in jeopardy of what??????? What are you protecting this from??? Exactly???????
:-?LIFE Safety circuits, not on GFCI. I do not do residential, but!
Who would put a smoke alarm system on a General use circuit with other outlets in there own house?
210.12 Arc-Fault Circuit-Interrupter Protection.
FPN No. 2: See 11.6.3(5) of NFPA 72?-2007, National Fire Alarm Code?, for information related to secondary power supply requirements for smoke alarms installed in dwelling units.
Exception No. 2: Where a branch circuit to a fire alarm system installed in accordance with 760.41(B) and 760.121(B) is installed in RMC, IMC, EMT, or steel armored cable, Type AC, meeting the requirements of 250.118, with metal outlet and junction boxes, AFCI protection shall be permitted to be omitted.
:-?LIFE Safety circuits, not on GFCI. I do not do residential, but!
Who would put a smoke alarm system on a General use circuit with other outlets in there own house?
210.12 Arc-Fault Circuit-Interrupter Protection.
FPN No. 2: See 11.6.3(5) of NFPA 72?-2007, National Fire Alarm Code?, for information related to secondary power supply requirements for smoke alarms installed in dwelling units.
Exception No. 2: Where a branch circuit to a fire alarm system installed in accordance with 760.41(B) and 760.121(B) is installed in RMC, IMC, EMT, or steel armored cable, Type AC, meeting the requirements of 250.118, with metal outlet and junction boxes, AFCI protection shall be permitted to be omitted.
Who would put a smoke alarm system on a General use circuit with other outlets in there own house?
210.12 Arc-Fault Circuit-Interrupter Protection.
FPN No. 2: See 11.6.3(5) of NFPA 72?-2007, National Fire Alarm Code?, for information related to secondary power supply requirements for smoke alarms installed in dwelling units.
Exception No. 2: Where a branch circuit to a fire alarm system installed in accordance with 760.41(B) and 760.121(B) is installed in RMC, IMC, EMT, or steel armored cable, Type AC, meeting the requirements of 250.118, with metal outlet and junction boxes, AFCI protection shall be permitted to be omitted.
Was Just a Question Guys
DETERMINATION:
…..
New construction shall meet the requirements of the prevailing Oregon Electrical Specialty Code and Oregon Residential Specialty Code, however, smoke detectors, nurse call, fire alarm or dedicated medical equipment shall not be required to be installed on AFCI protected circuits.
Thank you:smile:
DETERMINATION:
?..
New construction shall meet the requirements of the prevailing Oregon Electrical Specialty Code and Oregon Residential Specialty Code, however, smoke detectors, nurse call, fire alarm or dedicated medical equipment shall not be required to be installed on AFCI protected circuits.
918-305-0130(2)
210.12 Arc-Fault Circuit-Interrupter Protection.
?
(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits
supplying outlets installed in dwelling unit bedrooms shall be protected by a listed
arc-fault circuit interrupter, combination-type, installed to provide protection of
the branch circuit.
FPN No. 1: For information on types of arc-fault circuit interrupters, see UL 1699-
1999, Standard for Arc-Fault Circuit Interrupters.
FPN No. 2: See 11.6.3(5) of NFPA 72?-2007, National Fire Alarm Code?, for
information related to secondary power supply requirements for smoke alarms installed
in dwelling units.
FPN No. 3: See 760.41(B) and 760.121(B) for power-supply requirements for fire
alarm systems.
Exception No 1: Where RMC, IMC, EMT or steel armored cable, Type AC, meeting the
requirements of 250.118 using metal outlet and junction boxes is installed for the
portion of the branch circuit between the branch-circuit overcurrent device and the first
outlet, it shall be permitted to install a combination AFCI at the first outlet to provide
protection for the remaining portion of the branch circuit.
Exception No 2: Where a branch circuit to a fire alarm system installed in accordance
with 760.41(B) and 760.121(B) is installed in RMC, IMC, EMT, or steel armored cable,
type AC, meeting the requirements of 250.118, with metal outlet and junction boxes,
AFCI protection shall be permitted to be omitted.
Exception No 3: Electrical outlets dedicated for the use of single station smoke
alarms (interconnected or not), nurse call, or medical equipment shall not be required
to have AFCI protection.
...and here is the current specialty code.
Exception No 3: Electrical outlets dedicated for the use of single station smoke
alarms (interconnected or not), nurse call, or medical equipment shall not be required
to have AFCI protection.
I Have the NEC CD, Loose Leaf Binder and Soft Cover. all first Drafts.
None have Exception 3
Time to Get ERRATA DATA from Nfpa web site.
The CMP clearly intended the smoke detectors to be on an AFCI.
We need to protect the wiring to the smokes. Its the same as any other wiring. Plus smokes have battery backup.
Effective Dec 31, 2008 in washington state they may be on an AFCI but not required to.
My point is your posts:
clearly show you have not read or understood 210.12.
I just went through the 2005 on afcis and I have no Idea what you are refrencing from the posts. I agree that outlets get smashd all the time by furniture and case fires. I agree that aluminum wireing causes fires from poor connections. I dont agree at all that a low current circuit with devices mounted on the ceiling are in any danger of physical damage that could cause a fire. I dont agree that the low current devices are likely to cause a fire. I doubt a smoke detector/alarm ever caused a fire. This is my point
I just went through the 2005 on afcis and I have no Idea what you are refrencing from the posts.
I agree that outlets get smashd all the time by furniture and case fires. I agree that aluminum wireing causes fires from poor connections. I dont agree at all that a low current circuit with devices mounted on the ceiling are in any danger of physical damage that could cause a fire.
I dont agree that the low current devices are likely to cause a fire. I doubt a smoke detector/alarm ever caused a fire.