Smoke detectors vs Smoke alarms

Merry Christmas
Status
Not open for further replies.

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I was referring to system fire alarm strobes not the local smoke alrms ;) like if someone in the building pulls a pull station then the occupants in the building should be notified through strobes in their dwelling units.We need a 75db in the sleeping area as per NFPA 72 but do we require one outside the sleeping area per NFPA?

Ahhh, well I guess I misunderstood. However, if you go back to post #12, the section cited (29.5) refers to both smoke detectors and notification appliances meeting the same requirements as smoke alarms in 29.5.1. So, if you have a smoke alarm with an integral sounder outside the sleeping area, I would propose you'll need at least a horn in the same location to make some noise if you're using a regular fire alarm system.
 

shortcircuit1

Senior Member
Location
USA
Ahhh, well I guess I misunderstood. However, if you go back to post #12, the section cited (29.5) refers to both smoke detectors and notification appliances meeting the same requirements as smoke alarms in 29.5.1. So, if you have a smoke alarm with an integral sounder outside the sleeping area, I would propose you'll need at least a horn in the same location to make some noise if you're using a regular fire alarm system.

You are right!I should read it more carefully!:thumbsup:
 

LIM

Member
Location
NC
2013 NFPA 72

29.3.6 All audible fire alarm signals installed shall meet the
performance requirements of 18.4.3, 18.4.5.1, 18.4.5.2, and
29.3.8.


18.4.5 Sleeping Area Requirements.
18.4.5.1* Where audible appliances are installed to provide
signals for sleeping areas, they shall have a sound level of at
least 15 dB above the average ambient sound level or 5 dB
above the maximum sound level having a duration of at least
60 seconds or a sound level of at least 75 dBA, whichever is
greater, measured at the pillow level in the area required to be
served by the system using the A-weighted scale (dBA).
18.4.5.2 If any barrier, such as a door, curtain, or retractable
partition, is located between the notification appliance and
the pillow, the sound pressure level shall be measured with the
barrier placed between the appliance and the pillow.
18.4.5.3* Effective January 1, 2014, audible appliances provided
for the sleeping areas to awaken occupants shall produce a low
frequency alarm signal that complies with the following:
(1) The alarm signal shall be a square wave or provide equivalent
awakening ability.
(2) The wave shall have a fundamental frequency of 520 Hz
± 10 percent.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
2013 NFPA 72

29.3.6 All audible fire alarm signals installed shall meet the
performance requirements of 18.4.3, 18.4.5.1, 18.4.5.2, and
29.3.8.


18.4.5 Sleeping Area Requirements.
18.4.5.1* Where audible appliances are installed to provide
signals for sleeping areas, they shall have a sound level of at
least 15 dB above the average ambient sound level or 5 dB
above the maximum sound level having a duration of at least
60 seconds or a sound level of at least 75 dBA, whichever is
greater, measured at the pillow level in the area required to be
served by the system using the A-weighted scale (dBA).
18.4.5.2 If any barrier, such as a door, curtain, or retractable
partition, is located between the notification appliance and
the pillow, the sound pressure level shall be measured with the
barrier placed between the appliance and the pillow.
18.4.5.3* Effective January 1, 2014, audible appliances provided
for the sleeping areas to awaken occupants shall produce a low
frequency alarm signal that complies with the following:
(1) The alarm signal shall be a square wave or provide equivalent
awakening ability.
(2) The wave shall have a fundamental frequency of 520 Hz
± 10 percent.

Very important! I keep forgetting about that. :slaphead:
 

webcrest

Banned
Location
pakistan
smoke alarms are more sensitive.

smoke alarms are more sensitive.

i think smoke alarms are more sensitive. like if you burn food in the kitchen, or have too many people smoking in the house, it will set it off.
 
Last edited by a moderator: