Just a thought, I have done alot of troubleshooting being that I work in a modular plant as a tester for few years. I have seen alot of different and alot of times out right weird things cause problems with gfcis and now afcis. I'll mention a couple of them to keep a eye on, hopefully this helps with some of your service call backs.
1, Wire staples driven to tight or bent to far. Didn't matter if they were insulated or not. It also didn't matter if there bend radius was to code. We figured out if you drive the staple just enough to be snug and still have plents of room to let the wire move freely under the staple alot of these problems went away. As far as bends are concerned we started using the way I was taught, which is to bend the wire around the handle of a screw driver at all bend points, this fixed all with wire bends.
2, Small nicks in conductors do to cable rippers or utility knife. Whick became simply an awareness issue.
3, Grounds tied together from different circuits, Yikes.
4, Loose connections.
5, To much wire inside a box.
Most of these problems will show up in a dielectric strength test. Which I strongly reccomend doing.
Hope this helps.