danickstr said:If I have smokes in each bedroom, do I need to put one in a connecting hall that is only 6 feet long? It has a low ceiling and the owner says it will look stupid, and I agree. The bedrooms are at each end, and the hall spills into a dining kitchen area.
peter d said:Not according to the NEC. This question will be answered in your local fire and/or building codes.
In this area, the answer would be yes. We are required to have a smoke/CO detector outside of the sleeping area.
Rich Elec. said:11.5.1.1 (2) Outside of each seperate dwelling unit sleeping area, within 21ft of any door to a sleepng room, the distance measured along a path of travel.
As others have mentioned, this is a code that is generally imposed by State authorities. Here in NJ we are required to have both interconnected smoke alarms in the bedroom area and smoke and CO detectors in common hallways irrespective of the size of the area. The CO detectors are not required to be interconnected with the smoke alarms and can be plug-in units, if desired. BTW, the last job I did I used combination Firex units in this area and after numerous fault conditions that caused the units to chirp and after I replaced them 3 times I finally changed them over to smoke alarms and plug-in CO units.danickstr said:If I have smokes in each bedroom, do I need to put one in a connecting hall that is only 6 feet long?
Again, as others have stated, don't get caught up in ridiculous comments made by homeowners. Cite the code to them and let them take their own time to go down to the township and see if they can apply for a "variation in the code" (quite different than a variance) and see how far they get.It has a low ceiling and the owner says it will look stupid,
danickstr said:I knew this was not a NEC thing but we do end up installing these things, so I thought I would ask...
I appreciate all the answers.
I would be interested to know if it is 12 or 21 feet from the door of the sleeping room, since I could qualify the kitchen one that is already there at 21 feet.
Rich Elec. said:The NEC would not be your best resource when designing a fire alarm system. You should check in NFPA 72 - National Fire Alarm Code.
That's a common phrase these days.danickstr said:i assume that...
wbalsam1 said:In NY State, smokes are required on every level of the home, in each sleeping space and adjacent to each sleeping space and a CO detector is required on the lowest level that has sleeping. The smokes are required to be interconnected so that when one alarms, they all do. They're also required to have battery backup. Also the CO detector is required to be on a lighting circuit ahead of any intervening switches. :smile:
If they are going by NFPA 72, I've paraphrased it here.danickstr said:I knew this was not a NEC thing but we do end up installing these things, so I thought I would ask...
21 feet, by NFPA 72.I would be interested to know if it is 12 or 21 feet from the door of the sleeping room, since I could qualify the kitchen one that is already there at 21 feet.
this was not code related, but rather one person's commentary.831 said:That's a common phrase these days.![]()