What is the code for smoke detectors in a dwelling?
Hew George how about in the immidate vicenity outside the bedroom?georgestolz said:Where are smoke detectors required to be installed, and where do I find this information?
NFPA 72 and various building codes have different specific requirements, but in general:
One in each bedroom (to wake people up).
One on each level, including basement.
If a ceiling on any level has an elevation change of 24", each elevation needs one. Example: Vaulted living room on same floor as 8' ceiling for back hall, den, laundry.
No closer than 3' to any cold air return or supply, or ceiling fan. Nuisance alarms due to dust attraction are common when this is done, and the sensitivity can diminish.
No closer than 4" to peak of vaulted ceiling, or wall edge. Smoke rolls in corners, bypassing detector.
No farther than 3' from peak of vaulted ceiling.
Interconnection of detectors is required.
Per 210.12, AFCI protection required.
Many smoke detectors come with instructions that mirror NFPA 72's requirements, so they could also be considered a 110.3(B) listing issue, if NFPA 72 has not been adopted in your area.
Here are some related threads, or you can search for the term "smoke detector" and find many results.
http://www.mikeholt.com/code_forum/s...ad.php?t=81410
http://www.mikeholt.com/code_forum/s...ad.php?t=78988
http://www.mikeholt.com/cgi-bin/codeforum/ultimatebb.cgi?ubb=get_topic;f=11;t=005755;p=1#000 005
I have heard that, but I don't recall seeing it. At the time I heard it, I thought it was a made-up code. Perhaps someone with NFPA 72 could clear this up?Hew George how about in the immidate vicenity outside the bedroom?
To answer your question there is no code for smoke detectors in the NEC. In our state (NC) it is in the building code-- I suspect it is there in other states as well.awhelectric said:What is the code for smoke detectors in a dwelling?
stickboy1375 said:We're required to install CO's outside of bedroom areas, so I just make it a smoke/CO combo unit...
R313.1 Single- and multiple-station smoke alarms. Single- and multiple-station smoke alarms shall be installed in the following locations:
1. In each sleeping room.
2. Outside of each separate sleeping area in the immediate vicinity of the bedrooms.
3. On each additional story of the dwelling, including basements and cellars but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level.
All smoke alarms shall be listed and installed in accordance with the provisions of this code and the household fire warning equipment provision of NFPA 72.
R313.2 Carbon monoxide alarms. In new residential structures regulated by this code that are equipped with fuel burning appliances, carbon monoxide alarms shall be installed on each habitable level. All carbon monoxide detectors shall be listed and comply with U.L. 2034 and shall be installed in accordance with provisions of this code and NFPA 720.
11.5.1.1 Smoke Detection. Where required by applicable laws, codes, or standards for the specified occupancy, approved single- and multiple-station smoke alarms shall be installed as follows:
(1) In all sleeping rooms
(2) Outside of each separate sleeping area, in the immediate vicinity of the sleeping rooms
(3) On each level of teh dwelling unit, including basements.
raider1 said:(2) Outside of each separate sleeping area, in the immediate vicinity of teh sleeping rooms
mark henderson said:Raider I just looked in the 2007 NFPA72 and that line no reads
From NFPA 72 11.5.1.1(2)
Ooutside of each seprate dwelling unit sleeping area, within 6.4m (21ft) of any door to a sleeping room, the distance measured along a path of travel.
Mark
PS. sorry about the whole quote thing I wont get so happy with that from now on.
dcooper said:All the Fire Dept around herre are not excepting CO/SM combo. They want 2 separate systems.
dcooper said:I live in MA and each Fire Dept. is different.. They are the authority having juristiction and ALWAYS win.
In my read of 72 this morning, I noticed a requirement ("shall") for photoelectric smokes if the detector is placed within 20' of a cooking appliance. I had thought it was a good design feature, rather than an actual requirement.cpal said:but in your case if you are using the ionization combination detectors they maybe correct in failing the installtion when located with in 20 feet of a bath or kitchen. \\at this time I still do not think that there is a combo unit on the market with photo electric smokes.
georgestolz said:I had thought it was a good design feature, rather than an actual requirement.
I haven't read the MA code posted above, however.
From what I've heard and seen in my state, I believe 72 is enforced without adoption, but I can't be sure of that.