I believe Kidde has moved to all photoelectric as of quite recently. No more ionization. I could be wrong, but I think the listing criteria for smoke alarms changed, so everyone is moving away from ionization.
Both Kidde and First Alert have full hardwired, hardwired power but wirelessly interconnected alarms, and battery powered with wireless interconnection models. X-Sense on Amazon also has some listed wireless options, if you want to trust an Amazon brand.
2024 International Residential Code
R310.2.2 Alterations, repairs and additions.
Where alterations, repairs or additions requiring a permit occur, the individual dwelling unit shall be equipped with smoke alarms located as required for new dwellings.
Exceptions:
1. Work involving the exterior surfaces of dwellings, such as the replacement of roofing or siding, the addition or replacement of windows or doors, or the addition of a porch or deck
2. Installation, alteration or repairs of plumbing or mechanical systems.
R310.4 Interconnection.
Where more than one smoke alarm is required to be installed within an individual dwelling unit in accordance with
Section R310.3, the alarm devices shall be interconnected in such a manner that the actuation of one alarm will activate all of the alarms in the individual dwelling unit. Physical interconnection of smoke alarms shall not be required where listed wireless alarms are installed and all alarms sound upon activation of one alarm.
R310.6 Power source.
Smoke alarms shall receive their primary power from the building wiring where such wiring is served from a commercial source and, where primary power is interrupted, shall receive power from a battery. Wiring shall be permanent and without a disconnecting switch other than those required for overcurrent protection.
Exceptions:
- Smoke alarms shall be permitted to be battery operated where installed in buildings without commercial power.
- Smoke alarms installed in accordance with Section R310.2.2 shall be permitted to be battery powered.