junkhound
- Renton, WA
- EE, power electronics specialty
WR GFCI installed on puget sound shoreling, appox 40 feet above high tide, Maury Island. Fully covered outlet boxes, the big ugly clear plastic type.
HO reported numerous trips, so turned off CB to area of outdoor convienience outlets.
Had HO turn on breaker with meter on outlet, dead, cannot reset, but GFCI makes buzzing sound for a few seconds then slight smoke, no 'snap' or other arcing sounds, just the faint buzz and slight smoke.
Replaced the outlet, all is well
Out of curiosity, disassembled the GFCI. HO had reported a storm a few seeks earlier had thrown sea splash 50 feet high.
Salt water got past the terminals, enough conductivity on the plastic to enable low current arcing from GFCI solenoid to plastic.