I would say this would be non-compliant. Many of the icemakers I've seen would be considered quite stationary.Do snap switches that control lighting require in front clearnances? i have an architect leaving me eight inches of clearance between the ice maker and a bank of light switches. Thanks guys!!
You do not have enough space to do maintenance...that is replace the switch.110.26 Spaces About Electrical Equipment.
Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
You might make a case that this is a violation of the very first part of 110.26(A).
You do not have enough space to do maintenance...that is replace the switch.
However it is my position that all electrical equipment is "likely to require examination, adjustment, servicing, or maintenance while energized" and therefore all electrical equipment is covered by 110.26(A). This position is based on the CMP refusing to accept proposals to clarify what this section actually covers. I am sure they have no intention of making it apply to switches and receptacles, but as it is now written it does. It even makes it a violation of this section to install the required kitchen counter receptacles.
You might make a case that this is a violation of the very first part of 110.26(A).
You do not have enough space to do maintenance...that is replace the switch.
i have an architect leaving me eight inches of clearance
Charlie,I agree with Bob (break out the baloons! ). I think it is reasonable to say that there are certain things that are not likely to be worked on live, and I would include snap switches in this group.
That's Bob's problem, not the NEC's problem, and not the AHJ's problem. I am confident that he is up to the challenge. The NEC does not tell us anything about that subset of electrical equipment that does not require live work. It does not say that we must keep any minimum space for the convenience of the future maintenance worker.. . . how is he sure that the circuits are deenergized?
I didn't mean the posts in this thread, I meant the posts on the forum in general that indicate that a lot of work on energized equipment like this is occuring in the field.Don, of course I read all the posts, before I added my own opinion.
Again given the comments in this forum and the things I see in the field, it remains my opinion that this type of equipment is likely to be worked on while energized.And I disagree with your take on the present wording. The code does not say "all electrical equipment." The fact that there is a phrase like "likely to require . . . " tells me the CMP is allowing for the possibility that there will be some things with wires attached that are "not likely . . . ."
Examination would include troubleshooting and that often "requires" the circuit to be energized.Please note also the presence of the word, "require." The text does not say "likely to get worked on by some fool who should know better." It says "likely to require . . . ." Why should we infer that everything is "likely to require. . . "?
Please note also the presence of the word, "require."
given the comments in this forum and the things I see in the field, it remains my opinion that this type of equipment is likely to be worked on while energized.
Examination would include troubleshooting and that often "requires" the circuit to be energized.
My real point is that this is just very poor code and that the CMP refuses to accept proposals that will clear this up.
Code aside, I've seen hard-plumbed and -wired ice makers, and I wouldn't want to have to use stubbies and mirrors.
This is one installation I would want an inspector to fail. Yech!