Snow melting

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have outdoor snow melting equipment for gas station. Says they are going to provide 20A for light and snowmelting equipment. The circuit can share with conduit of light in parking lot. Would snowmelting circuit be shared with light circuit in one conduit or not NEC 2014? Anyone know
 
Last edited:
No reason can't be shared, subject to wire fill and derating.
Snowmelting requires GFPE OR GFCI, see mfgs instructions
 