JuliaTruchsess
Member
- Location
- Newtown, CT, USA
- Occupation
- Engineer
With THHN etc and Type W portable cord, the NEC tables provide ampacities at various insulation temperatures, so they can be used to ensure compliance with 110.14(C), e.g. if you have 75C terminations you use the 75C column of the table.
Table 400.5(A)(1) for SO, SOW, SOO, SOOW etc cord, however, does not have temperature columns - I guess it assumes that all SO is 90C? So how is one supposed to verify compliance with 110.14(C)? Measure the temperature under load? Makes it difficult to plan in advance.
Table 400.5(A)(1) for SO, SOW, SOO, SOOW etc cord, however, does not have temperature columns - I guess it assumes that all SO is 90C? So how is one supposed to verify compliance with 110.14(C)? Measure the temperature under load? Makes it difficult to plan in advance.